 EzFlora - missing zones
Hello
I am using Indigo 4.02 and just installed a EzFlora to replace my Irritrol RD-600 with 5 zones. Everything installed properly, but I am only showing zones 1, 2, and 4. Zones 3 and 5 are grayed out. I have checked the connections, re-installed the wires on zone 3 and 5 with the same result.
Any assistance is greatly appreciated.
Thanks,
Rod
Jun 24, 2009 6:25:42 PM
Sent INSTEON "EzFlora - zone4" on (ack: all valves off)
Sent INSTEON "EzFlora - zone4" off (ack: all valves off)
Sent INSTEON "EzFlora - zone1" off (ack: all valves off)
Sent INSTEON "EzFlora - zone2" off (ack: all valves off)
Sent INSTEON "EzFlora - zone3" off (ack: all valves off)
Sent INSTEON "EzFlora - zone5" off (ack: all valves off)
Sent INSTEON "EzFlora - zone6" off (ack: all valves off)
Sent INSTEON "EzFlora - zone7" off (ack: all valves off)
Sent INSTEON "EzFlora - zone8" off (ack: all valves off)
Jun 24, 2009 6:36:47 PM
WebServer Indigo Touch client connected from 10.0.1.1
Jun 24, 2009 6:42:36 PM
PowerLinc Linking - syncing PowerLinc links (address 0E.16.84)
PowerLinc Linking - . . . read: INSTEON plc link to controller 01.71.6F, flags 03, group 01, data 00 00 FF
PowerLinc Linking - comparing local and powerlinc links
PowerLinc Linking - . . match: remote link is identical to new link 01.71.6F, flags 03, group 01
PowerLinc Linking - compare complete
PowerLinc Linking - sync complete
PowerLinc Linking - initializing remote device "EzFlora" (address 01.71.6F, firmware version 2.4)
PowerLinc Linking - . enabling: valve status change broadcasting
PowerLinc Linking - received module button pressed from 01.71.6F
PowerLinc Linking - received module button pressed from 01.71.6F
PowerLinc Linking - . reading: pump control status and zone maximum durations
PowerLinc Linking - . forcing: internal valve selection
PowerLinc Linking - . . . read: pump control is disabled for valve 8
PowerLinc Linking - . . . read: zone maximum durations 80, 4, 0, 36, 0, 0, 0, 0
PowerLinc Linking - . . . read: zone enabled flags 0B
PowerLinc Linking - initialize complete
PowerLinc Linking - device "EzFlora" properties updated
PowerLinc Linking - syncing remote device "EzFlora" (address 01.71.6F, firmware version 2.4)
PowerLinc Linking - syncing of this device type not possible remotely (skipping)
PowerLinc Linking - sync complete
PowerLinc Linking - device "EzFlora" links updated
|
|
rodhugo
Joined: Dec 08, 2008 Posts: 2
|
 Figured it out
The max duration times were set to 0 for the other zones. Changed that, now it works.
|