[ANSWERED]: Action Group Not working as intended

Posted on
Sun Mar 06, 2016 3:18 am
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

[ANSWERED]: Action Group Not working as intended

I was wondering anyone else has seen what is happening to me and what the fix maybe.

In one action group I have named Night I set just about every device to turn off with the exceptions of a few like Camera go Active and Lamps in the Living Room and Master Bedroom go on for 3 Minutes then back off.

A Variable is set and the action Group is triggered with the variable change. It has worked flawless for awhile now until a few weeks ago. One light ......the outside spotlights turns on when this groups executes. It is the only one and it only happened sometimes.

I have already tried removing it from the action group and adding it back.
I also made sure it is set to off and not toggle.
Now I am syncing it again.

What else could it be?


Thanks in advance for any help.

Posted on
Sun Mar 06, 2016 7:16 am
jalves offline
Posts: 749
Joined: Jun 16, 2013

Re: Action Group Not working as intended

When you removed the outside lights from the group did it then work properly? ..and then when you add it back the problem resumes? If so, you might have some kind of "noise" problem with that controller.

Running Indigo 2023.2 on a 24" iMac M1), OS X 14.4
Jeff

Posted on
Sun Mar 06, 2016 7:20 am
akimball offline
Posts: 561
Joined: Aug 07, 2013
Location: Sandy, Utah

Re: Action Group Not working as intended

It may help to know the types of devices you're turning on and off along with the actual script youre executing.

I have found that delaying a few devices by a second or more will sometimes help.
I've discovered that including KeypadLinc's can sometimes lead to issues.
I've discovered that some insteon devices like the inLineLinc's can never be a controller....only a responder.

These are a few of the complexities which may be affecting your reliability.

-Al

Posted on
Sun Mar 06, 2016 9:23 am
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: Action Group Not working as intended

akimball wrote:
It may help to know the types of devices you're turning on and off along with the actual script youre executing.

I have found that delaying a few devices by a second or more will sometimes help.
I've discovered that including KeypadLinc's can sometimes lead to issues.
I've discovered that some insteon devices like the inLineLinc's can never be a controller....only a responder.

These are a few of the complexities which may be affecting your reliability.


The Outside Lights are on a simple GE Lightswitch. My entire house uses the same switches and it worked fine for months. It just started doing it.

jalves wrote:
When you removed the outside lights from the group did it then work properly? ..and then when you add it back the problem resumes? If so, you might have some kind of "noise" problem with that controller.


After I removed it from the Action Group and added it back it again worked fine for several days but last night when I switched it to Night the lights went on.


This is an image of the action group. The problem light is Outside Spotlights back.

Image

Posted on
Sun Mar 06, 2016 11:19 am
matt (support) offline
Site Admin
User avatar
Posts: 21424
Joined: Jan 27, 2003
Location: Texas

Re: Action Group Not working as intended

The next time it doesn't work correctly, copy/paste the Event Log window contents showing what Indigo did. If Indigo said it sent an OFF command, then that it what it told the interface to perform. If instead the module turned ON, then there is a signal problem or the module if malfunctioning.

Image

Posted on
Thu Mar 17, 2016 5:08 am
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: [ANSWERED]: Action Group Not working as intended

Matt,

From the time I made the original post until last night the action group worked as intended. Last night when I fired the night action I noticed it turned on the outside spotlights instead of sending an off request. I had already had my main computer off and couldn't screen shot the log file. I did however screen shot it on the mobile app which shows an on request.

I am not convinced it is the module because I also noticed last night it isn't limited to that module. It also turned on the garage lights and sent an open request to the garage door (linear Garage Door Opener) via Veralite Bridge App.

My next step is going to be to completely destroy the action group and build it again.

Posted on
Thu Mar 17, 2016 8:06 am
matt (support) offline
Site Admin
User avatar
Posts: 21424
Joined: Jan 27, 2003
Location: Texas

Re: [ANSWERED]: Action Group Not working as intended

Indigo stores 30 days of log files, so if you can open the file from last night and copy/paste the lines for the time chunk of when it occurred then we can better help troubleshoot the problem.

Image

Posted on
Thu Mar 17, 2016 10:50 am
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: [ANSWERED]: Action Group Not working as intended

Matt,

Here is the Log


2016-03-16 23:39:59.940 Trigger Night
2016-03-16 23:39:59.941 Action Group Night
2016-03-16 23:39:59.977 Vera Bridge vera thread: sent "Garage Door Opener" off
2016-03-16 23:39:59.979 Sent Hue Lights "Living Room - Lamp" on to 40 at ramp rate 4.0 sec.
2016-03-16 23:39:59.980 Trigger Living Hue - Color Temp
2016-03-16 23:40:00.066 Z-Wave sent "Dinning Room Dimmer" off
2016-03-16 23:40:00.082 Sent Hue Lights "Master Bath Hue 1" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.084 Vera Bridge vera thread: sent "Schlage Deadbolt" lock
2016-03-16 23:40:00.095 Z-Wave sent "Dinning Room Recepticle (Wax Burner)" off
2016-03-16 23:40:00.124 Z-Wave sent "Dinning Room Recepticle (Xmas Tree)" off
2016-03-16 23:40:00.178 Sent Hue Lights "Media Room - Couch Lamp" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.268 Z-Wave sent "Foyer Light" off
2016-03-16 23:40:00.277 Sent Hue Lights "Media Room Bath 1" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.289 Z-Wave sent "Foyer Recepticle (Xmas)" off
2016-03-16 23:40:00.312 Z-Wave sent "Garage Lights" off
2016-03-16 23:40:00.343 Z-Wave sent "Kitchen Island Fan Light" off
2016-03-16 23:40:00.373 Z-Wave sent "Kitchen Recessed Dimmer" off
2016-03-16 23:40:00.376 Sent Hue Lights "Media Room Bath 2" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.478 Sent Hue Lights "Media Room Bath 3" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.579 Sent Hue Lights "TV Lightstrip" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.678 Sent Hue Lights "Media Room Lamp (End Table Hue)" off at ramp rate 0.0 sec.
2016-03-16 23:40:00.680 Hue Lights Error Cannot set Color Temperature values. The "Living Room - Lamp" device does not support variable color tmperature.
2016-03-16 23:40:01.920 Z-Wave sent "Kitchen Recpticle (Coffee Pot)" off
2016-03-16 23:40:01.948 Z-Wave sent "Kitchen Sink Dimmer" off
2016-03-16 23:40:01.979 Z-Wave sent "Laundry Room Light" off
2016-03-16 23:40:02.216 Z-Wave sent "Living Room Light" off
2016-03-16 23:40:02.250 Z-Wave sent "Living Room Recepticle (TV East Wall)" off
2016-03-16 23:40:02.278 Z-Wave sent "Living Room Recepticle (Xmas Tree)" off
2016-03-16 23:40:02.303 Z-Wave sent "Master Bedroom Fan" off
2016-03-16 23:40:02.331 Z-Wave sent "Master Bedroom Lamp" set brightness to 20
2016-03-16 23:40:02.366 Z-Wave sent "Master Bedroom Light " off
2016-03-16 23:40:02.398 Z-Wave sent "Master Bedroom Recepticle (TV)" on
2016-03-16 23:40:02.427 Z-Wave sent "Media Bath Ceiling Fan" off
2016-03-16 23:40:02.458 Z-Wave sent "Media Bath Ceiling Heat" off
2016-03-16 23:40:02.487 Z-Wave sent "Media Bath Ceiling Light" off
2016-03-16 23:40:02.516 Z-Wave sent "Utility Room" off
2016-03-16 23:40:02.548 Z-Wave sent "Media Pendant" off
2016-03-16 23:40:02.582 Z-Wave sent "Media Recessed" off
2016-03-16 23:40:02.615 Z-Wave sent "Media Room- Reading Lamp" off
2016-03-16 23:40:02.713 Z-Wave sent "Outside Deck " off
2016-03-16 23:40:02.859 Z-Wave sent "Outside Front GFI" off
2016-03-16 23:40:03.004 Z-Wave sent "Outside Front Porch" off
2016-03-16 23:40:03.033 Z-Wave sent "Outside Front Sofet Lights" off
2016-03-16 23:40:03.062 Z-Wave sent "Outside Spotlights Back" off
2016-03-16 23:40:09.039 Z-Wave received "Laundry Room Light" energy total to 20.230 kWh
2016-03-16 23:40:10.469 Updated "Living Room - Lamp" on to 29
2016-03-16 23:40:10.778 Z-Wave received "Foyer Motion Sensor" status update is on
2016-03-16 23:40:10.780 Trigger Foyer Motion Light On
2016-03-16 23:40:10.816 Z-Wave sent "Foyer Light" on
2016-03-16 23:40:30.505 Updated "Living Room - Lamp" on to 40
2016-03-16 23:40:33.150 Z-Wave received "Kitchen Motion Sensor" status update is on
2016-03-16 23:40:33.152 Trigger Turn Kitchen Light On
2016-03-16 23:40:33.250 Z-Wave sent "Kitchen Recessed Dimmer" set brightness to 40
2016-03-16 23:40:33.784 Trigger Garage Door Open
2016-03-16 23:40:33.785 Trigger Garage Door Lights
2016-03-16 23:40:33.826 Z-Wave sent "Garage Lights" on
2016-03-16 23:40:33.848 Z-Wave sent "Outside Spotlights Back" on
2016-03-16 23:40:33.849 Trigger Outside Spotlight Back Light Timer Start
2016-03-16 23:40:48.085 Z-Wave received "Media Room - Motion Sensor" status update is off
2016-03-16 23:41:03.346 Z-Wave received "Media Room - Motion Sensor" status update is on
2016-03-16 23:41:03.348 Trigger Turn Media Room Reading Lamp On
2016-03-16 23:41:03.387 Z-Wave sent "Media Room- Reading Lamp" set brightness to 80
2016-03-16 23:41:10.318 Schedule Foyer Motion Light On (delayed action)
2016-03-16 23:41:10.407 Z-Wave sent "Foyer Light" off
2016-03-16 23:41:27.859 Z-Wave received "Media Bath Luminance" sensor update to 2 lux
2016-03-16 23:41:27.861 Z-Wave received "Media Bath Humidity" sensor update to 47%
2016-03-16 23:41:27.908 Z-Wave received "Media Bath Temperature" sensor update to 68.2 °F
2016-03-16 23:41:37.683 Z-Wave received "Outside Spotlights Back" status update is off
2016-03-16 23:41:39.173 Z-Wave received "Meter Total" power load to 721.405 W
2016-03-16 23:41:39.216 Z-Wave received "Meter Total" energy total to 926.085 kWh
2016-03-16 23:41:39.346 Z-Wave received "Meter Clamp 1" power load to 213.920 W
2016-03-16 23:41:39.430 Z-Wave received "Meter Clamp 2" power load to 507.485 W
2016-03-16 23:41:39.520 Z-Wave received "Meter Clamp 1" energy total to 476.115 kWh
2016-03-16 23:41:39.646 Z-Wave received "Meter Clamp 2" energy total to 449.970 kWh
2016-03-16 23:41:41.891 Z-Wave received "Media Room - Motion Sensor" status update is off
2016-03-16 23:41:41.893 Trigger Media Light Timer Start
2016-03-16 23:41:53.445 Z-Wave received "Foyer Motion Sensor" status update is off
2016-03-16 23:41:59.317 Schedule Night (delayed action)
2016-03-16 23:41:59.358 Sent Hue Lights "Living Room - Lamp" off at ramp rate 4.0 sec.
2016-03-16 23:42:01.352 Z-Wave received "Foyer Motion Sensor" status update is on
2016-03-16 23:42:01.354 Trigger Foyer Motion Light On
2016-03-16 23:42:01.392 Z-Wave sent "Foyer Light" on
2016-03-16 23:42:31.619 Z-Wave received "Foyer Motion Sensor" status update is off
2016-03-16 23:42:55.886 Z-Wave received "Kitchen Motion Sensor" status update is off
2016-03-16 23:42:55.888 Trigger Kitchen Light Timer Start
2016-03-16 23:43:01.317 Schedule Foyer Motion Light On (delayed action)
2016-03-16 23:43:01.328 Z-Wave received "Kitchen Motion Sensor" status update is on
2016-03-16 23:43:01.330 Trigger Kitchen Light Timer Pause
2016-03-16 23:43:01.352 Z-Wave sent "Foyer Light" off
2016-03-16 23:43:24.173 Z-Wave received "Foyer Motion Sensor" status update is on
2016-03-16 23:43:24.175 Trigger Foyer Motion Light On
2016-03-16 23:43:24.210 Z-Wave sent "Foyer Light" on
2016-03-16 23:43:30.218 Z-Wave received "Media Room - Motion Sensor" status update is on
2016-03-16 23:43:30.219 Trigger Media Light Timer Pause
2016-03-16 23:43:31.652 Z-Wave received "Media Room Door Sensor" status update is on
2016-03-16 23:43:31.654 Trigger Media Room Lights On (Recessed)
2016-03-16 23:43:31.694 Z-Wave sent "Media Recessed" on
2016-03-16 23:43:38.550 Z-Wave received "Garage Lights" status update is off
2016-03-16 23:43:40.542 Z-Wave received "Media Room Door Sensor" status update is off
2016-03-16 23:43:49.619 Z-Wave received "Media Recessed" status update is off
2016-03-16 23:44:17.249 WebServer Indigo Touch client connected from 192.168.1.215
2016-03-16 23:44:17.885 Z-Wave received "Kitchen Motion Sensor" status update is off
2016-03-16 23:44:17.887 Trigger Kitchen Light Timer Start
2016-03-16 23:44:20.372 Z-Wave received "Media Room - Motion Sensor" status update is off
2016-03-16 23:44:20.374 Trigger Media Light Timer Start
2016-03-16 23:44:24.315 Schedule Foyer Motion Light On (delayed action)
2016-03-16 23:44:24.365 Z-Wave sent "Foyer Light" off
2016-03-16 23:44:28.474 Vera Bridge vera thread: sent "Garage Door Opener" off
2016-03-16 23:44:31.365 Trigger Garage Door Closed
2016-03-16 23:44:33.316 Schedule Garage Door Lights (delayed action)
2016-03-16 23:44:33.351 Z-Wave sent "Outside Spotlights Back" off
2016-03-16 23:45:01.885 Z-Wave received "Kitchen Motion Sensor" status update is on
2016-03-16 23:45:01.887 Trigger Kitchen Light Timer Pause
2016-03-16 23:45:31.315 Schedule Media Room Lights On (Recessed) (delayed action)
2016-03-16 23:45:31.401 Z-Wave sent "Media Recessed" off
2016-03-16 23:45:32.452 Z-Wave received "Foyer Motion Sensor" status update is off
2016-03-16 23:45:33.316 Schedule Garage Door Lights (delayed action)
2016-03-16 23:45:33.373 Z-Wave sent "Garage Lights" off
2016-03-16 23:45:39.177 Z-Wave received "Meter Total" power load to 457.453 W
2016-03-16 23:45:39.261 Z-Wave received "Meter Total" energy total to 926.133 kWh
2016-03-16 23:45:39.348 Z-Wave received "Meter Clamp 1" power load to 205.887 W
2016-03-16 23:45:39.485 Z-Wave received "Meter Clamp 2" power load to 251.566 W
2016-03-16 23:45:39.526 Z-Wave received "Meter Clamp 1" energy total to 476.131 kWh
2016-03-16 23:45:39.663 Z-Wave received "Meter Clamp 2" energy total to 450.002 kWh
2016-03-16 23:45:44.273 Z-Wave received "Foyer Motion Sensor" status update is on
2016-03-16 23:45:44.275 Trigger Foyer Motion Light On
2016-03-16 23:45:44.309 Z-Wave sent "Foyer Light" on
2016-03-16 23:46:14.632 Z-Wave received "Foyer Motion Sensor" status update is off
2016-03-16 23:46:38.901 Z-Wave received "Kitchen Motion Sensor" status update is off
2016-03-16 23:46:38.903 Trigger Kitchen Light Timer Start
2016-03-16 23:46:44.315 Schedule Foyer Motion Light On (delayed action)
2016-03-16 23:46:44.381 Z-Wave sent "Foyer Light" off
2016-03-16 23:47:39.133 Trigger Kitchen Light (Auto Off 2Min)
2016-03-16 23:47:39.856 Z-Wave sent "Kitchen Recessed Dimmer" set brightness to 0
2016-03-16 23:47:51.791 Trigger Turn Off Lights Plex
2016-03-16 23:47:51.825 Z-Wave sent "Master Bedroom Light " off
2016-03-16 23:47:51.856 Z-Wave sent "Master Bedroom Lamp" off

Posted on
Thu Mar 17, 2016 11:23 am
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: [ANSWERED]: Action Group Not working as intended

Matt,

I may have figured part out. I have two Triggers setup to the garage door. "Garage Door Open" which just updates a variable and the other "Garage Door Lights" Which turns on the Garage Lights if it is dark out. That one also turns on the Outside Spotlights back since thats how I let my dog out. It has a delayed off after 5 minutes. It seems those two triggers are firing when I trigger Action Group Night.

Both Garage Triggers Look for State Change to become on so they shouldn't trigger as I am sending an Off trigger in Action Group Night. Any thoughts aside from taking Garage Door out of the Action Group. I been known to leave it open all night in the summer months. :-)

Posted on
Sat Mar 19, 2016 10:42 am
matt (support) offline
Site Admin
User avatar
Posts: 21424
Joined: Jan 27, 2003
Location: Texas

Re: [ANSWERED]: Action Group Not working as intended

Can you post screen shots of the Triggers, Conditions, and Actions panels for both "Garage Door Open" and "Garage Door Lights"? We need to see all the details to help troubleshoot what is occurring.

Image

Posted on
Sat Mar 19, 2016 12:27 pm
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: [ANSWERED]: Action Group Not working as intended

Didn't upload in proper order but that is both


Image

Image

Image

Image


Image


Image

Posted on
Sat Mar 19, 2016 1:41 pm
matt (support) offline
Site Admin
User avatar
Posts: 21424
Joined: Jan 27, 2003
Location: Texas

Re: [ANSWERED]: Action Group Not working as intended

Since your "Garage Door Open" is coming from Vera, can you check the Vera logs for the same time to see what it shows? I think the Vera Bridge plugin is getting a message from the Vera that the state for that device has become ON, which is what starts the triggers in Indigo.

Image

Posted on
Sat Mar 19, 2016 8:36 pm
Sharek326 offline
User avatar
Posts: 377
Joined: Jul 20, 2014
Location: Lansford, PA

Re: [ANSWERED]: Action Group Not working as intended

I logged into vera but Logging wasn't turned on until I just did it now. I am only able to see todays log files. I guess I will wait and see when and if it does it again.

Posted on
Mon Jan 22, 2018 4:37 pm
wideglidejrp offline
User avatar
Posts: 555
Joined: Jan 15, 2012
Location: Danbury, CT

Re: [ANSWERED]: Action Group Not working as intended

I have an action group question. Suppose I have an action group which calls several other action groups. Is there a way to put a pause before or after an action group?

John R Patrick
Author of
Home Attitude

Posted on
Mon Jan 22, 2018 4:56 pm
Colorado4Wheeler offline
User avatar
Posts: 2794
Joined: Jul 20, 2009
Location: Colorado

Re: [ANSWERED]: Action Group Not working as intended

You can use the delay feature but it may not be exactly what you are wanting, it is probably more reliable to just do a quick Python script with delays between the execute statements - depending on how much you want to delay.

My Modest Contributions to Indigo:

HomeKit Bridge | Device Extensions | Security Manager | LCD Creator | Room-O-Matic | Smart Dimmer | Scene Toggle | Powermiser | Homebridge Buddy

Check Them Out Here

Page 1 of 1