Inconsistent behaviour

Posted on
Mon Jan 04, 2021 5:38 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Inconsistent behaviour

Hi Jon, Might be missing something there, but these 2 rooms seem to be behaving differently

Screenshot 2021-01-04 at 11.28.53.png
Screenshot 2021-01-04 at 11.28.53.png (42.82 KiB) Viewed 3867 times


At approx 15:00 the temp sensor goes above the Stat SP and the TRV SP is set to 8 c from its overriden value 3 degrees above the Stat SP and the valve goes off.

However on this one

Screenshot 2021-01-04 at 11.36.20.png
Screenshot 2021-01-04 at 11.36.20.png (50.07 KiB) Viewed 3867 times


The plug in doesnt seem to adjust the TRV SP to 8 and so it continues to manage the temperature to the overriden TRV SP using the valve % so the room maintains at a higher temperature than the desired set point.

Both use remote temperature sensors and appear to have the same settings.

Any ideas?
Thanks
Simon

Posted on
Mon Jan 04, 2021 7:55 am
autolog offline
Posts: 3991
Joined: Sep 10, 2013
Location: West Sussex, UK [GMT aka UTC]

Re: Inconsistent behaviour

Hi Simon.
Happy New Year to you. :D

Looking at the second image, both the Remote and TRV set-points seem to be going to 8C between 14:00 and 17:00?

So unless I am missing something, it looks OK?

Posted on
Mon Jan 04, 2021 7:59 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Inconsistent behaviour

Happy new year to you too.

It’s at 18:00 where I’d expect the TRV set point to go to 8 as the room temp was higher than the desired set point

Posted on
Mon Jan 04, 2021 8:12 am
autolog offline
Posts: 3991
Joined: Sep 10, 2013
Location: West Sussex, UK [GMT aka UTC]

Re: Inconsistent behaviour

I agree, it doesn't seem correct. :(

Are you sure that the Remote Stat is being used to monitor the temperature? I know you probably are, but just double checking.

Because, if it was using the TRV temperature to monitor the temp, it would be correct.

Posted on
Wed Nov 10, 2021 3:05 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

Hi Jon. Its that time of year again and realised that this strange behaviour is still happening on the twins' thermostat.
Its not setting the setpoint on the TRV to 8 once the remote temperature reaches the plugin setpoint of 20.

Any ideas what might be going wrong?
Attachments
Screenshot 2021-11-10 at 09.03.18.png
Screenshot 2021-11-10 at 09.03.18.png (402.74 KiB) Viewed 3378 times
Screenshot 2021-11-10 at 09.03.05.png
Screenshot 2021-11-10 at 09.03.05.png (441.63 KiB) Viewed 3378 times
Screenshot 2021-11-10 at 08.59.15.png
Screenshot 2021-11-10 at 08.59.15.png (51.82 KiB) Viewed 3378 times

Posted on
Wed Nov 10, 2021 3:48 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

Interestingly I was getting this behaviour on another room and created a new TRV controller device with what I thought were same settings, moved all the dependencies over and deleted the original device.
The behaviour is now as expected, ie the TRV setpoint goes to 8 when the remote temperature sensor is higher than the controller setpoint.

Is it possible that the old device has not properly captured the remote sensor despite it showing in the GUI?

Posted on
Wed Nov 10, 2021 9:02 am
autolog offline
Posts: 3991
Joined: Sep 10, 2013
Location: West Sussex, UK [GMT aka UTC]

Re: Inconsistent behaviour

Hi Simon,
I agree it looks odd. :?

Is there anything special about the Twin Temp piBeacon and is that the same stat in other room that is working OK?

You could try the procedure you use in the other room to correct it on the twins' room, to see if that resolves it.

Other than that, I would probably need to see some debugging logs for the time period it happens in order to see if that throws any light on the issue?

Posted on
Wed Nov 10, 2021 10:58 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

Yes I’ve recreated a trv controller device. Copied settings from the screenshots on here and deleted the old one. Initial impressions are that it now work as expected whereas the old one didn’t.

Posted on
Thu Nov 11, 2021 1:31 pm
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

I have turned on debugging on the plugin and will try some tests this evening. One of the rooms where I recreated a new device is still not setting the TRV SP back to 8 so will try and capture an event to share.

Posted on
Thu Nov 11, 2021 5:31 pm
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

I set the trv controller to 21 at 19:20 and it did some weird behaviour. The TRV isnt 5 degrees higher and the the TRV is not set to 8 when the remote temp exceeds the set point.
Attachments
Screenshot 2021-11-11 at 23.22.19.png
Screenshot 2021-11-11 at 23.22.19.png (74.33 KiB) Viewed 3277 times

Posted on
Fri Nov 12, 2021 2:25 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

Morning Jon,
This is strange.. schedule set to set study to 21 with a 5 degree offset. Except the setpoint on the trv controller as well as the trv itself are both set to 26.

edit: when I reloaded the TRV plugin, the controller SP was reverted to 21 as it should be and the valve then went to off.

This seems to be the relevant bit of code. The setpointHeat was at 21 and setPointTRV at 26 for a second or 2, then the TRV seems to go to TRV hardware control and the setpointHeat goes to 26. There is a weird line with the setpoint at 119.8 at 08:00:17.348

Code: Select all
======================================================================================================================================================
==
==  Method: 'deviceUpdated'
==  Sequence: 78302
==  Device: TRV - 'Study TRV'
==  Last Communication: 2021-11-12 08:00:05
==  List of states to be queued for update by TRVHANDLER:
==    > Description = UPDATE ZWAVE EVENT SENT TRV, Value = 2021-11-12 08:00:17
==  Description of updates that will be performed by TRVHANDLER:
==    > TRV Z-Wave event sent. Time updated to '2021-11-12 08:00:17'. Sent count now totals: 158
==
======================================================================================================================================================


2021-11-12 08:00:17.296   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 1, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.298   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 1, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.300   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.301   THREADDEBUG    Plugin.method.zwaveCommandReceived      Main Plugin Method
2021-11-12 08:00:17.301   THREADDEBUG    Plugin.method.controlTrvHeatingOn       TrvHandler Method
2021-11-12 08:00:17.304   DEBUG          Plugin.general.zwaveCommandReceived     

ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ
ZZ
ZZ  TRV Z-WAVE > RECEIVE INTERCEPTED: 01 0C 00 04 00 7F 06 31 05 01 42 06 9B 64 (node 127)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 12, Class = Sensor Multilevel, Verb = Verb 05, Temperature = 16.91
ZZ
ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ


2021-11-12 08:00:17.312   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.310   THREADDEBUG    Plugin.method.controlHeatingSource      TrvHandler Method
2021-11-12 08:00:17.320   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '4' [MAX = '8'] <=======
2021-11-12 08:00:17.326   DEBUG          Plugin.trvHandler.controlHeatingSource      Control Heating Source: Thermostats calling for heat from Variable 'HeatReqdHallway':
  > Dining Room Thermostat
  > Study Thermostat

2021-11-12 08:00:17.327   DEBUG          Plugin.general.deviceUpdated             

======================================================================================================================================================
==
==  Method: 'deviceUpdated'
==  Sequence: 78303
==  Device: TRV - 'Study TRV'
==  Last Communication: 2021-11-12 08:00:05
==  List of states to be queued for update by TRVHANDLER:
==    > Description = UPDATE ZWAVE EVENT RECEIVED TRV, Value = 2021-11-12 08:00:17
==  Description of updates that will be performed by TRVHANDLER:
==    > TRV Z-Wave event received. Time updated to '2021-11-12 08:00:17'. Received count now totals: 165
==
======================================================================================================================================================


2021-11-12 08:00:17.332   DEBUG          Plugin.trvHandler.run                       
TRVHANDLER: 'Study Thermostat' DEQUEUED COMMAND 'UPDATE TRV STATES'
2021-11-12 08:00:17.333   THREADDEBUG    Plugin.method.updateDeviceStates        TrvHandler Method
2021-11-12 08:00:17.339   DEBUG          Plugin.trvHandler.updateDeviceStates       

XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
XX  Method: 'updateDeviceStates'
XX  Sequence: 78301
XX  Device: TRV CONTROLLER - 'Study Thermostat'
XX  List of states to be updated:
XX    > Description = UPDATE ZWAVE EVENT RECEIVED TRV, Value = 2021-11-12 08:00:17
XX  States to be updated in the TRV Controller device:
XX    > {'value': '2021-11-12 08:00:17', 'key': 'zwaveEventReceivedDateTimeTrv'}
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX


2021-11-12 08:00:17.339   THREADDEBUG    Plugin.method.zwaveCommandSent          Main Plugin Method
2021-11-12 08:00:17.339   THREADDEBUG    Plugin.method.controlTrv                TrvHandler Method
2021-11-12 08:00:17.348   DEBUG          Plugin.general.zwaveCommandSent         

ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ
ZZ
ZZ  TRV Z-WAVE > SEND INTERCEPTED: 01 0A 00 13 7F 03 43 02 01 25 77 88 (node 127 ACK after 17 milliseconds)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 10, Class = Thermostat Setpoint, Verb = Get, Setpoint = 119.0
ZZ  'TRV' device Z-WAVE > Pending: True, Sequence:  '2', Setpoint: '26.0'
ZZ
ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ


2021-11-12 08:00:17.352   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' is set to Controller Mode 'TRV UI Control'
2021-11-12 08:00:17.353   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.355   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 4, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.360   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '5' [MAX = '8'] <=======
2021-11-12 08:00:17.363   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 4, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.365   DEBUG          Plugin.general.deviceUpdated             

======================================================================================================================================================
==
==  Method: 'deviceUpdated'
==  Sequence: 78304
==  Device: TRV - 'Study TRV'
==  Last Communication: 2021-11-12 08:00:05
==  List of states to be queued for update by TRVHANDLER:
==    > Description = UPDATE CONTROLLER MODE, Value = 4
==    > Description = UPDATE ZWAVE EVENT SENT TRV, Value = 2021-11-12 08:00:17
==  Description of updates that will be performed by TRVHANDLER:
==    > Controller Mode updated from Auto Schedule Control to TRV UI Control
==    > TRV Z-Wave event sent. Time updated to '2021-11-12 08:00:17'. Sent count now totals: 159
==
======================================================================================================================================================


2021-11-12 08:00:17.368   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.369   THREADDEBUG    Plugin.method.controlTrvHeatingOn       TrvHandler Method
2021-11-12 08:00:17.382   THREADDEBUG    Plugin.method.controlHeatingSource      TrvHandler Method
2021-11-12 08:00:17.390   DEBUG          Plugin.trvHandler.controlHeatingSource      Control Heating Source: Thermostats calling for heat from Variable 'HeatReqdHallway':
  > Dining Room Thermostat
  > Study Thermostat

2021-11-12 08:00:17.390   THREADDEBUG    Plugin.method.zwaveCommandReceived      Main Plugin Method
2021-11-12 08:00:17.395   DEBUG          Plugin.trvHandler.run                       
TRVHANDLER: 'Study Thermostat' DEQUEUED COMMAND 'UPDATE TRV STATES'
2021-11-12 08:00:17.402   DEBUG          Plugin.general.zwaveCommandReceived     

ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ
ZZ
ZZ  TRV Z-WAVE > RECEIVE INTERCEPTED: 01 0C 00 04 00 7F 06 43 03 01 22 00 50 BD (node 127)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 12, Class = Thermostat Setpoint, Verb = Report, Setpoint = 8.0, Pending Controller Mode = TRV Hardware Control
ZZ
ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ


2021-11-12 08:00:17.402   THREADDEBUG    Plugin.method.updateDeviceStates        TrvHandler Method
2021-11-12 08:00:17.409   DEBUG          Plugin.trvHandler.updateDeviceStates       

XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
XX  Method: 'updateDeviceStates'
XX  Sequence: 78302
XX  Device: TRV CONTROLLER - 'Study Thermostat'
XX  List of states to be updated:
XX    > Description = UPDATE ZWAVE EVENT SENT TRV, Value = 2021-11-12 08:00:17
XX  States to be updated in the TRV Controller device:
XX    > {'value': '2021-11-12 08:00:17', 'key': 'zwaveEventSentDateTimeTrv'}
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX


2021-11-12 08:00:17.410   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.410   THREADDEBUG    Plugin.method.controlTrv                TrvHandler Method
2021-11-12 08:00:17.425   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '6' [MAX = '8'] <=======
2021-11-12 08:00:17.430   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' is set to Controller Mode 'TRV Hardware Control'
2021-11-12 08:00:17.432   DEBUG          Plugin.general.deviceUpdated             

======================================================================================================================================================
==
==  Method: 'deviceUpdated'
==  Sequence: 78305
==  Device: TRV - 'Study TRV'
==  Last Communication: 2021-11-12 08:00:05
==  List of states to be queued for update by TRVHANDLER:
==    > Description = UPDATE ZWAVE EVENT RECEIVED TRV, Value = 2021-11-12 08:00:17
==    > Description = UPDATE CONTROLLER MODE, Value = 3
==  Description of updates that will be performed by TRVHANDLER:
==    > TRV Z-Wave event received. Time updated to '2021-11-12 08:00:17'. Received count now totals: 166
==    > Controller Mode updated from Auto Schedule Control to TRV Hardware Control
==
======================================================================================================================================================


2021-11-12 08:00:17.435   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 3, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.438   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 3, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.438   THREADDEBUG    Plugin.method.zwaveCommandSent          Main Plugin Method
2021-11-12 08:00:17.441   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.446   DEBUG          Plugin.general.zwaveCommandSent         

ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ
ZZ
ZZ  TRV Z-WAVE > SEND INTERCEPTED: 01 09 00 13 7F 02 26 02 25 78 E1 (node 127 ACK after 7 milliseconds)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 9, Class = Switch Multilevel, Verb = Get, Get Valve Status
ZZ
ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ

Attachments
Screenshot 2021-11-12 at 08.22.10.png
Screenshot 2021-11-12 at 08.22.10.png (57.43 KiB) Viewed 3288 times
Screenshot 2021-11-12 at 08.24.29.png
Screenshot 2021-11-12 at 08.24.29.png (369.33 KiB) Viewed 3288 times

Posted on
Fri Nov 12, 2021 3:50 am
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

I have now started plotting the controllerMode in grafana and 2 of the TRV controllers are in mode 3, ie TRV Hardware Control, even though they havent been touched and have child lock on.

Restarting the plugin resets them to mode 0 Auto, but then they flip back to mode 3. Is this expected behaviour?

Posted on
Fri Nov 12, 2021 11:54 am
autolog offline
Posts: 3991
Joined: Sep 10, 2013
Location: West Sussex, UK [GMT aka UTC]

Re: Inconsistent behaviour

Hi Simon,

siclark wrote:
I have now started plotting the controllerMode in grafana and 2 of the TRV controllers are in mode 3, ie TRV Hardware Control, even though they havent been touched and have child lock on.

Restarting the plugin resets them to mode 0 Auto, but then they flip back to mode 3. Is this expected behaviour?


Just catching up with posts. :)

I don't think it is expected behaviour? I would expect it to go into that mode if the setpoint was changed on the TRV.

I will investigate for you. The trouble is, when I have touched the code for ages, it takes a while to remind myself how it all works, or doesn't as the case may be. :wink:

EDIT:
What version of the plugin are you running to make sure that I am looking at the relevant version?

Posted on
Fri Nov 12, 2021 12:32 pm
siclark offline
Posts: 1964
Joined: Jun 13, 2017
Location: UK

Re: Inconsistent behaviour

I did check with my wife that she didn’t touch the trv and in the other room I Was sat there the whole time.

The logging shows a lot of changing between modes on the 2 devices I recreated.

Image

Posted on
Fri Nov 12, 2021 1:44 pm
autolog offline
Posts: 3991
Joined: Sep 10, 2013
Location: West Sussex, UK [GMT aka UTC]

Re: Inconsistent behaviour

Yes, definitely looks odd; well spotted. :)

So, what version of the plugin are you running (you might have missed the edit on my previous post)?